program Universal;
// PIC pin assignment
//   PORTA.0 -> AN0 (battery voltage multiplied by R6/(R5+R6)) (analog IN)
//   PORTA.1 -> AN1 (current pickup) (analog IN)
//   PORTA.2 -> spare (OUT)
//   PORTA.3 -> spare  (Analog IN may be temperature reading)
//   PORTA.4 -> BUZZER (OUT)
//   PORTA.5 -> spare (OUT)
//   PORTB.0 -> FAN cooler (OUT)
//   PORTB.1 -> D4 data bus for display (OUT)
//   PORTB.2 -> D5 data bus for display (OUT)
//   PORTB.3 -> D6 data bus for display (OUT)
//   PORTB.4 -> D7 data bus for display (OUT)
//   PORTB.5 -> UP key (IN)
//   PORTB.6 -> DOWN key (IN)
//   PORTB.7 -> OK/ENTER key (IN)
//   PORTC.0 -> spare (OUT)
//   PORTC.1 -> PWM2 DISCHARGE (OUT)
//   PORTC.2 -> PWM1 CHARGE (OUT)
//   PORTC.3 -> RS register/data for display (OUT)
//   PORTC.4 -> RW read/write for display (OUT)
//   PORTC.5 -> E  enable for display  (OUT)
//   PORTC.6 -> TX  RS232 trasmit  (OUT)
//   PORTC.7 -> RX  RS232 receive (IN)
// Constants
const repeat_period = 16;                                                       //repeat key period -> 16*5ms = 80ms (about 12 press/sec)
      repeat_initial = 200;                                                     //initial delay for start autorepeat -> 200*5ms = 1000ms
      key_pressed = 10;                                                         //time to hit a key for a valid action -> 10*5ms = 50ms
      ctrl_period = 1;                                                          //CV charge BW control 1*5ms -> 200Hz BW (max)
//    EEPROM Memory map
//    247..255        //spare locations
      uni_profile = 246;                                                        //Position for the selected profile in EEPROM
      uni_maxcharge = 245;                                                      //Maximum allowable charge current 255 -> 255A
      uni_maxdischarge = 244;                                                   //Maximum allowable discharge current 255 -> 255A
      uni_beep = 243;                                                           //beep tone semiperiod 0..255
      uni_r6h = 242;                                                            //
      uni_r6l = 241;                                                            //R5=0..65535 in Ohm
      uni_r5h = 240;                                                            //
      uni_r5l = 239;                                                            //R6=0..65535 in Ohm
      uni_currh = 238;                                                          //
      uni_currl = 237;                                                          //current pick up sensitivity 0..65535 -> 65535uV/A
      uni_mode = 236;                                                           //idle, charge or discharge mode, see below constants
      uni_secondline = 220;                                                     //second hello line
      uni_firstline = 204;                                                      //first hello line
//    0..203        //space for the 12 profiles
//    Single profile map
      profilelen = 17;                                                          //single profile length
      pchemistry = 0;                                                           //parameters position in a specific profile: Chemistry
      pcapacity = 1;                                                            //capacity in mAh/100, 255 -> 25500mAh
      pncells = 2;                                                              //Number of cells
      pcharge = 3;                                                              //charge in capacity units 255 -> 25.5*capacity
      pdischarge = 4;                                                           //discharge in capacity units 255 -> 25.5*capacity
      pinhibit = 5;                                                             //Inhibit in minutes for delta peak check: 255 -> 255 min
      pcutoff_nicd = 6;                                                         //Cutoff in discharge for NiMh
      pcutoff_nimh = 7;                                                         //Cutoff in discharge for NiCd
      pcutoff_lipo = 8;                                                         //Cutoff in discharge for LiPo
      pcutoff_sla = 9;                                                          //Cutoff in discharge for SLA
      pdeltav_nicd = 10;                                                        //deltav in charge for NiCd
      pdeltav_nimh = 11;                                                        //deltav in charge for NiMh
      pmaxv_lipo = 12;                                                          //max voltage in charge for LiPo
      pmaxv_sla = 13;                                                           //max voltage in charge for SLA
      pfinalcurr_lipo = 14;                                                     //final current (% of initial) for LiPo
      pfinalcurr_sla = 15;                                                      //final current (% of initial) for SLA
      ptimeout = 16;                                                            //Timeout for charge
//    Constants for battery identification
      nicd = 0;        //battery codes: Nickel Cadmium
      nimh = 1;        //Nickel Metal Hydride
      lipo = 2;        //Lithium Polimer
      sla = 3;        //Sealed Lead Acid
//    Constants for charger action identification
      idle = 0;        //idle phase (for interrupt routine)
      discharge_cc = 1;                                                         //discharge at costant current (for interrupt routine)
      charge_cc = 2;                                                            //charge at costant current (for interrupt routine)
      charge_cv = 3;                                                            //charge at costant voltage (for interrupt routine)
//    Constants for charger last action identification
      mode_idle = 0;                                                            //idle mode for power interrupt
      mode_charge = 1;                                                          //charge phase for power interrupt
      mode_discharge = 2;                                                       //discharge phase for power interrupt
// Display messages
       msg_hello1='.seven-segments.';
       msg_hello2='www.        .com';
       msg_main1='Task select:    ';
       msg_main2='Profile select  ';
       msg_main3='Batt. charge    ';
       msg_main4='Batt. discharge ';
       msg_main7='Profile change  ';
       msg_main8='PC management   ';
       msg_main9='Volt calibr.    ';
       msg_main10='Ampere calibr.  ';
       msg_change1='Chemistry:      ';
       msg_change2='Battery type    ';
       msg_change3='NiCd';
       msg_change4='NiMh';
       msg_change5='LiPo';
       msg_change6='SLA ';
       msg_change7='Capacity:       ';
       msg_change8='mAh per cell    ';
       msg_change9='Cells:          ';
       msg_change10='Number of cells ';
       msg_change11='Charge:         ';
       msg_change12='mult. for capac.';
       msg_change13='Discharge:      ';
       msg_change15='Name:           ';
       msg_pcman1='PC serial link..';
       msg_discharge='Dsch.';
       msg_charge='Chrg.';
       msg_end='End!';
       msg_display='Pack#';
       msg_init='Initializing... ';
// Variables
var i:byte;        //generic interrupt
    tempw:word;
    tempi:integer;
    ii,j,k,l,m,n,act:byte;                                                      //generic program
    tw,tw1,tw2,vrat,pk,maxcap,ilim:word;
    tlw,tlw1:longint;
    twi:integer;
    tmpword:string[5];
    tmpbyte:string[3];
    repeat_counter:byte;                                                        //keys
    repeat_flag:byte;
    repeat_k1,repeat_k2,repeat_k3:byte;
    keys:byte;
    msec,sec,minu:byte;                                                         //time
    count_slow:byte;                                                            //analog values
    fast_voltage:word;
    slow_voltage:word;
    acc_voltage:longint;
    fast_current:word;
    slow_current:word;
    acc_current:longint;
    action:byte;        //task to be performed: charge, discharge...
    duty_pwm_charge,duty_pwm_discharge:integer;                                 //pwm control (mosfet drive)
    target_current:word;                                                        //target current for costant current phases
    target_voltage:word;                                                        //target voltage for costant voltage phases
    zero_current:word;
    mah:longint;        //amount of charge
    menupos:byte;                                                               //top menu position
    selprof:byte;                                                               //profile selection index
    selitem:byte;                                                               //item selected within the change profile routine
    profile_point:byte;                                                         //current profile selected
    eevar,eelim,eeres:byte;                                                     //eeprom variables
    phase,q,ps:byte;                                                            //current phase for power interrupt handling
    pt,pw:word;
    bdelay:byte;
    cbeep,dbeep,ebeep,kk:byte;
    calibra:byte;
    tempib:integer;
    slow_voltageb,pwmb:word;
    mahb:longint;
    pwm_err:byte;
    ctrl_co,ctrl_flag:byte;
// PWM adjust
procedure setpwm;
begin
  CCPR1L:=duty_pwm_charge shr 2;                                                //PWM1 is phisically connected to the charge FET
  CCP1CON.5:=duty_pwm_charge.1;
  CCP1CON.4:=duty_pwm_charge.0;
  CCPR2L:=duty_pwm_discharge shr 2;                                             //PWM2 is phisically connected to the discharge FET
  CCP2CON.5:=duty_pwm_discharge.1;
  CCP2CON.4:=duty_pwm_discharge.0;
end;
// Interrupt, every 5msec -> keyboard, sampling ANx, control loops for  voltage and current, TX UART
procedure interrupt;
begin
  if INTCON.2 = 1 then
  begin
    TMR0 := 0x3D;                                                               //an interrupt every 5ms
    INTCON.2:=0;
// Internal clock
    inc(msec);        //clock
    if (msec=200) then
      begin
        msec:=0;
        inc(sec);                                                               //one second is 200 interrupts
      end;
    if (sec=60) then
      begin
        sec:=0;
        inc(minu);                                                              //one minute is 60 seconds
      end;
// This unit controls the bndwitdh for CV charge
    inc(ctrl_co);
    if (ctrl_co=ctrl_period) then
      begin
        ctrl_co:=0;
        ctrl_flag:=1;                                                           //When this flag is high the CV control will be peformed
      end
    else
      begin
        ctrl_flag:=0;
      end;
// Keyboard management
    inc(repeat_counter);                                                        //counter for key repetition
    if (repeat_counter=repeat_period) then
      begin
        repeat_counter:=0;
        repeat_flag:=1;                                                         //when this flag is high is simulated a "key hit"
      end
    else
      begin
        repeat_flag:=0;
      end;
    if PORTB.6 = 0 then                                                         //if one key has been pressed, (this is the "DOWN" or "-" key)
      begin
        if (repeat_k1<>repeat_initial) then inc(repeat_k1);                     //increase the "key pressed" counter
        if (repeat_k1=key_pressed) then
          begin
            keys.0:=1;
          end;
        if (repeat_k1=repeat_initial) then
          begin
            if (repeat_flag=1) then keys.0:=1;
          end;
      end
    else
      begin
        repeat_k1:=0;
      end;
    if PORTB.5 = 0 then
      begin
        if (repeat_k2<>repeat_initial) then inc(repeat_k2);                     //increase the "key pressed" counter (this is the "UP" or "+" key)
        if (repeat_k2=key_pressed) then
          begin
            keys.1:=1;
          end;
        if (repeat_k2=repeat_initial) then
          begin
            if (repeat_flag=1) then keys.1:=1;
          end;
      end
    else
      begin
        repeat_k2:=0;
      end;
    if PORTB.7 = 0 then
      begin
        if (repeat_k3<>repeat_initial) then inc(repeat_k3);                     //increase the "key pressed" counter (this is the "OK" or "NEXT" key)
        if (repeat_k3=key_pressed) then
          begin
            keys.2:=1;
          end;
        if (repeat_k3=repeat_initial) then
          begin
            if (repeat_flag=1) then keys.2:=1;
          end;
      end
    else
      begin
        repeat_k3:=0;
      end;
// sampling the cells voltage and current
    tempw:=0;
    ADCON0:=0x81;
    delay_us(5);
    for i:=0 to 63 do
      begin
        ADCON0.2:=1;
        repeat until ADCON0.2=0;
        tempw:=tempw+ADRESL;
        tempw:=tempw+(ADRESH shl 8);
      end;
    fast_voltage:=tempw;                                                        //voltage and current @16bits
    acc_voltage:=acc_voltage+tempw;
    tempw:=0;
    ADCON0:=0x89;
    delay_us(5);
    for i:=0 to 63 do
      begin
        ADCON0.2:=1;
      end;
    fast_current:=tempw;                                                        //voltage and current @16bits
    acc_current:=acc_current+tempw;
    inc(count_slow);
    if (count_slow=0) then
      begin
        slow_voltage:=acc_voltage shr 8;                                        //voltage and current @16bits "high precision"
        slow_current:=acc_current shr 8;                                        //voltage and current @16bits "high precision"
        acc_voltage:=0;
        acc_current:=0;
      end;
    case (action) of                                                            //choice for different operating modes
// Discharge at constant current (all the batteries)
    discharge_cc:begin                                                          //discharge control loop
        tempi:=fast_current-zero_current;
        if (tempi<0) then tempi:=0;
        mah:=mah+tempi;
        if (tempi>target_current) then                                          //modulate the PWM following the discharge current changes
          begin
            dec(duty_pwm_discharge);
            if (duty_pwm_discharge<0) then duty_pwm_discharge:=0;
          end
        else
          begin
            inc(duty_pwm_discharge);
            if (duty_pwm_discharge>1023) then
              begin
                duty_pwm_discharge:=1023;
                pwm_err:=1;                                                     //if the PWM is at the maximum value, there is an error
              end;
          end;
      end;
// Charge at constant current (NiMh and NiCd all the time, LiPo and SLA only the first period)
    charge_cc:begin                                                             //charge cc control loop
        tempi:=zero_current-fast_current;
        if (tempi>0) then mah:=mah+tempi;
        if (tempi>target_current) then                                          //modulate the PWM following the charge current changes
          begin
            dec(duty_pwm_charge);
            if (duty_pwm_charge<0) then duty_pwm_charge:=0;
          end
        else
          begin
            inc(duty_pwm_charge);
            if (duty_pwm_charge>1023) then
              begin
                duty_pwm_charge:=1023;
              end;
          end;
      end;
// Charge at costant voltage (LiPo and SLA second period)
    charge_cv:begin                                                             //charge cv control loop
          begin
            dec(duty_pwm_charge);                                               //In any case saturate at the maximum charge current
          end
        else
          begin
            if (ctrl_flag=1) then                                               //decrease the bandwidth
              begin
                if (fast_voltage>target_voltage) then                           //modulate the PWM following the cells voltage changes
                  begin
                  end
                else
                  begin
                      begin
                      end;
                  end;
              end;
          end;
      end
// Idle
    else        //otherwise reset all
      begin
        duty_pwm_charge:=0;
      end;
    end;
    setpwm;        //update the PWM hardware with the most recent values
//  during any charge or discharge TX via serial I/F the values
    if (action<>0) then
      begin
        i:=count_slow and 15;
        case i of
          0:TXREG:=0x55;                                                        //4 0x55 values for syncing with PC
          1:TXREG:=0x55;
          2:TXREG:=0x55;
          3:begin
              TXREG:=0x55;                                                      //latches the multibyte values
              if (action=1) then
                begin
                  tempib:=slow_current-zero_current;
                  pwmb:=duty_pwm_discharge;
                end
              else
                begin
                  tempib:=zero_current-slow_current;
                  pwmb:=duty_pwm_charge;
                end;
              slow_voltageb:=slow_voltage;
              mahb:=mah;
            end;
          4:TXREG:=hi(pwmb);                                                    //output of all the parameters, one for 5ms slot, total 16*5=80ms
          5:TXREG:=lo(pwmb);
          6:TXREG:=hi(tempib);
          7:TXREG:=lo(tempib);
          8:TXREG:=hi(slow_voltageb);
          9:TXREG:=lo(slow_voltageb);
          10:TXREG:=highest(mahb);
          11:TXREG:=higher(mahb);
          12:TXREG:=hi(mahb);
          13:TXREG:=lo(mahb);
          14:TXREG:=minu;
          15:TXREG:=sec;
        end;
      end;
  end;
end;
// Procedure delay in milliseconds
procedure delayms(a:byte);
begin
  for bdelay:=1 to a do delay_ms(1);
end;
// procedure click for key feedback
procedure click;
begin
  for ebeep:=1 to 5 do
    begin
      PORTA.4:=ebeep.0;
      delayms(1);
    end;
end;
// procedure single beep at user defined frequency
procedure beep;
begin
  INTCON.GIE:=0;
  cbeep:=eeprom_read(uni_beep);
  for dbeep:=1 to 201 do
    begin
      PORTA.4:=dbeep.0;
      for ii:=1 to cbeep do delay_us(10);
    end;
  INTCON.GIE:=1;
end;
// Three beep for end of charge and discharge
procedure tribeep;
begin
  for kk:=1 to 3 do
    begin
      beep;
      delayms(200);
    end;
end;
// Display management routines
procedure lcd4(a,b:byte);                                                       //a command code, b=0 command, b=1 data;
begin
  PORTC.3:=b.0;
  PORTC.4:=0;
  PORTB.1:=a.4;
  PORTB.2:=a.5;
  PORTB.3:=a.6;
  PORTB.4:=a.7;
  PORTC.5:=1;        //generic 4 bit command or data write
  PORTC.5:=0;
  PORTB.1:=a.0;
  PORTB.2:=a.1;
  PORTB.3:=a.2;
  PORTB.4:=a.3;
  PORTC.5:=1;
  PORTC.5:=0;
  delay_us(1000);
end;
procedure lcd8(a:byte);
begin
  PORTC.3:=0;
  PORTC.4:=0;
  PORTB.1:=a.4;
  PORTB.2:=a.5;        //generic 8 bit command write
  PORTB.3:=a.6;
  PORTB.4:=a.7;
  PORTC.5:=1;
  PORTC.5:=0;
end;
procedure cls;
begin
  lcd4(1,0);
  delayms(5);
end;
procedure lcd_df_config;
begin
  INTCON.GIE:=0;
  delayms(1);        //start with 8 bit interface
  lcd8(0x30);
  delayms(10);
  lcd8(0x30);
  delayms(10);
  lcd8(0x30);
  delayms(10);
  lcd8(0x20);
  delayms(10);
  lcd4(0x28,0);        //now we are on 4 bit interface
  lcd4(0x0C,0);
  lcd4(6,0);
  cls;
  delayms(250);
  lcd4(0x80,0);
  lcd4(32,1);        //write a space to test
  cls;        //clear all
  INTCON.GIE:=1;
end;
procedure lcd_df_out(a:byte;p:word);
begin
  pt:=p;
  lcd4(a,0);
  repeat
    pw:=flash_read(pt);
    q:=lo(pw);
    if (q<>0) then lcd4(q,1);
    inc(pt);
  until (q=0);
end;
procedure lcd_df_out_eeprom(a:byte;p:byte);
begin
  ps:=p;
  lcd4(a,0);
  for j:=0 to 15 do
    begin
      q:=eeprom_read(ps+j);
      lcd4(q,1);
    end;
end;
procedure lcd_df_char(a,c:byte);  //a:command code, b:character
begin
  lcd4(a,0);
  lcd4(c,1);
end;
// Main menu for functions activation
procedure main_menu;
begin
   repeat
     lcd_df_out(128,@msg_main1);                                                //clear display and write msg_main1
     case menupos of
       0:lcd_df_out(192,@msg_main2);
       1:lcd_df_out(192,@msg_main3);
       2:lcd_df_out(192,@msg_main4);
       3:lcd_df_out(192,@msg_main7);
       4:lcd_df_out(192,@msg_main8);
       5:lcd_df_out(192,@msg_main9);
       6:lcd_df_out(192,@msg_main10);
     end;
     keys:=0;
     repeat until (keys<>0);
     click;
     if (keys.0=1) then
       begin
         dec(menupos);
         if (menupos=255) then menupos:=0;
       end;
     if (keys.1=1) then
       begin
         inc(menupos);
         if (menupos=7) then menupos:=6;
       end;
   until (keys.2=1);
end;
// Procedure display profile
procedure lcd_profile;
begin
  lcd_df_out(128,@msg_display);
  l:=selprof;
  inc(l);
  bytetostr(l,tmpbyte);
  lcd_df_char(133,tmpbyte[1]);
  lcd_df_char(134,tmpbyte[2]);
  lcd_df_char(135,':');
  l:=eeprom_read(profile_point+pchemistry);
  case l of
    nicd:lcd_df_out(136,@msg_change3);
    nimh:lcd_df_out(136,@msg_change4);
    lipo:lcd_df_out(136,@msg_change5);
    sla:lcd_df_out(136,@msg_change6);
  end;
  lcd_df_char(141,'x');
  l:=eeprom_read(profile_point+pncells);
  lcd_df_char(142,tmpbyte[1]);
  lcd_df_char(143,tmpbyte[2]);
  l:=eeprom_read(profile_point+pcapacity);
  tw:=l*100;
  wordtostr(tw,tmpword);
  lcd_df_char(192,'K');
  lcd_df_char(193,tmpword[0]);
  lcd_df_char(194,tmpword[1]);
  lcd_df_char(195,tmpword[2]);
  lcd_df_char(196,tmpword[3]);
  lcd_df_char(197,tmpword[3]);
  l:=eeprom_read(profile_point+pcharge);
  lcd_df_char(198,'C');
  lcd_df_char(199,tmpbyte[0]);
  lcd_df_char(200,tmpbyte[1]);
  lcd_df_char(201,'.');
  lcd_df_char(202,tmpbyte[2]);
  l:=eeprom_read(profile_point+pdischarge);
  lcd_df_char(203,'D');
  lcd_df_char(204,tmpbyte[0]);
  lcd_df_char(205,tmpbyte[1]);
  lcd_df_char(206,'.');
  lcd_df_char(207,tmpbyte[2]);
end;
// Battery profile selection
procedure selprofile;
begin
  selprof:=eeprom_read(uni_profile);
  repeat
    lcd_profile;
    keys:=0;        //reset the key pressed and wait for one key
    click;
    if (keys.0=1) then
      begin
        dec(selprof);                                                           //key down -> decrease the profile pointer
        if (selprof=255) then selprof:=0;
        profile_point:=selprof*profilelen;
      end;
    if (keys.1=1) then
      begin
        inc(selprof);                                                           //key up -> increase the profile pointer
        if (selprof=12) then selprof:=11;
      end;
  until (keys.2=1);
  eeprom_write(uni_profile,selprof);                                            //update the profile selector EEPROM location
end;
// procedure A to ADU and viceversa
function atoadu:word;                                                           //tw1 argument in A*100,result in ADU
begin
  tw:=eeprom_read(uni_currh)*256+eeprom_read(uni_currl);                        //tw holds the uV/A for the current to voltage transducer (25000 for LTS25NP)
  tlw:=tw1*tw;
  result:=tlw/7629;
end;
function adutoa:word;                                                           //tw1 argument in ADU, result in A*100
begin
  tlw:=tw1*7629;
  result:=tlw/tw;
end;
// procedure mV to ADU and viceversa
function mvtoadu:word;                                                          //tw1 argument in mV, result in ADU
begin
  vrat:=(eeprom_read(uni_r5h) shl 8)+eeprom_read(uni_r5l);                      //R5
  tw:=(eeprom_read(uni_r6h) shl 8)+eeprom_read(uni_r6l);                        //R6
  tlw:=tw shl 12;                                                               //R6*4096
  tlw1:=tw+vrat;        //R5+R6
  tlw:=tlw/tlw1;        //R5*4096/(R5+R6)
  tlw:=(tw1*tlw) shl 1;                                                         //mV*(R6/(R5+R6))*65536
  result:=tlw/625;                                                              //mV*(R6/(R5+R6))*(65536/5000)
end;
function adutomv:word;                                                          //tw1 argument in ADU,result in mV
begin
  tlw:=vrat shl 12;                                                             //R5*4096
  tlw:=4096+(tlw/tw);                                                           //K=(1+R5/R6)*4096
  tlw:=tlw*tw1;        //ADU*4096*(1+R5/R6)/4096
  result:=tlw/53687;                                                            //ADU*(1+R5/R6)*(5000/65536)
end;
// procedure mah ADU to display mah
function recallmah:word;                                                          //result in mah
begin
  tw:=highest(mah) shl 8;
  tw:=tw+higher(mah);
  tlw:=6944*tw;
  tlw:=tlw/tw;
  result:=tlw;
end;
// procedure prepare display for charge and discharge (& other)
procedure prepdis(a:byte);
begin
  lcd_df_out(128,@msg_init);
  for ii:=1 to 30 do delayms(100);
  zero_current:=slow_current;                                                   //sample the "no current" level
  cls;
  l:=eeprom_read(profile_point+pcapacity);                                      //l holds the capacity divided by 100 -> 40 = 4000mAh
  tw:=l;
  if (a=0) then l:=eeprom_read(profile_point+pdischarge)                        //l holds the user rate multiplied by 10 -> 20 = 2.0C
           else l:=eeprom_read(profile_point+pcharge);
  tw1:=l*tw;        //target current in A*100 -> 40*20=800 discharge current (8.00A)
  if (a=0) then l:=eeprom_read(uni_maxdischarge)
           else l:=eeprom_read(uni_maxcharge);
  tw2:=l*100;
  if tw1>tw2 then tw1:=tw2;                                                     //saturate if the current exceed the charger capabilities
  target_current:=atoadu;                                                       //convert the value in ADU
  lcd_df_char(143,'A');
  lcd_df_char(198,'V');
  if calibra=0 then
    begin
      if (a=0) then lcd_df_out(128,@msg_discharge)
               else lcd_df_out(128,@msg_charge);
      lcd_df_char(205,'m');
      lcd_df_char(206,'A');
      lcd_df_char(207,'h');
    end;
  act:=eeprom_read(profile_point+pchemistry);                                   //read the chemistry
end;
// display management during charge and discharge
procedure displ;
begin
  tw:=adutoa;        //current display in format xx.xx
  lcd_df_char(138,tmpword[1]);
  lcd_df_char(139,tmpword[2]);
  lcd_df_char(140,'.');
  lcd_df_char(141,tmpword[3]);
  lcd_df_char(142,tmpword[4]);
  tw1:=slow_voltage;                                                            //voltage display in format xx.xxx
  tw:=adutomv;
  lcd_df_char(192,tmpword[0]);
  lcd_df_char(193,tmpword[1]);
  lcd_df_char(194,'.');
  lcd_df_char(197,tmpword[4]);
  if (calibra=0) then                                                           //if not in calibration,
    begin
      tw:=recallmah;                                                            //capacity display in format xxxxx
      lcd_df_char(200,tmpword[0]);
      lcd_df_char(201,tmpword[1]);
      lcd_df_char(202,tmpword[2]);
      lcd_df_char(203,tmpword[3]);
      lcd_df_char(204,tmpword[4]);
    end;
end;
// Charge routine
procedure charge;
begin
  cls;        //clear display
  eeprom_write(uni_mode,mode_charge);                                           //set the charge flag in case the action will be interrupted
  PORTB.0:=1;        //fan ON
  prepdis(1);        //prepare the display for charge
  ii:=eeprom_read(profile_point+pncells);
  m:=eeprom_read(profile_point+ptimeout);
  case act of
    0:begin        //read values for NiCd
        l:=eeprom_read(profile_point+pdeltav_nicd);
        n:=eeprom_read(profile_point+pinhibit);
        lcd_df_out(133,@msg_change3);
        tw1:=ii*l;
      end;
    1:begin
        l:=eeprom_read(profile_point+pdeltav_nimh);                             //read values for NiMh
        lcd_df_out(133,@msg_change4);
        tw1:=ii*l;
      end;
    2:begin
        l:=eeprom_read(profile_point+pmaxv_lipo);                               //read values for LiPo
        n:=eeprom_read(profile_point+pfinalcurr_lipo);
        lcd_df_out(133,@msg_change5);
        tw:=3500+(l shl 2);
        tw1:=ii*tw;
      end;
    3:begin
        l:=eeprom_read(profile_point+pmaxv_sla);                                //read values for SLA
        n:=eeprom_read(profile_point+pfinalcurr_sla);
        lcd_df_out(133,@msg_change6);
        tw:=2000+(l shl 2);
        tw1:=ii*tw;
      end;
  end;
  target_voltage:=mvtoadu;                                                      //target voltage: deltaV for NiCd e NiMh, MaxV for LiPo e SLA
  j:=eeprom_read(profile_point+pcapacity);                                      //j holds the capacity divided by 100 -> 40 = 4000mAh
  maxcap:=j*m;        //maxcap holds the timeout-> cap*timeout=capacity for timeout escape
  tlw:=target_current*n;
  ilim:=tlw/100;        //ilim holds the value of current for end of charge in the CV phase
  action:=charge_cc;                                                            //starts the control
  mah:=0;        //reset the variables
  sec:=0;
  minu:=0;
  pk:=0;
  keys:=0;
  pwm_err:=0;
  repeat
    twi:=zero_current-slow_current;                                             //calculate the effective current
    if twi<0 then twi:=0;
    tw1:=twi;
    displ;        //display the values
    case act of
    0,1:begin
          if minu>n then                                                        //if NiXX charge, wait for end of inhibition
            begin
              INTCON.GIE:=0;
              if slow_voltage>pk then pk:=slow_voltage;                         //holds the peak
              twi:=pk-slow_voltage;
              INTCON.GIE:=1;
              if twi>target_voltage then action:=idle;                          //if under the delta peak, exit
            end;
        end;
    2,3:begin
          INTCON.GIE:=0;
          if (action=charge_cc) then if slow_voltage>target_voltage then action:=charge_cv;  //if LiXX charge stops the CC charge at max voltage
          if (action=charge_cv) then if twi<ilim then action:=idle;             //stops the charge if under final current
          INTCON.GIE:=1;
        end;
    end;
    tw:=recallmah;
    if (tw>maxcap) then action:=idle;
    if pwm_err=1 then action:=idle;
  until (keys.2=1) or (action=idle);
  action:=idle;
  eeprom_write(uni_mode,mode_idle);
  lcd_df_out(133,@msg_end);
  sec:=0;
  tribeep;
  keys:=0;
  repeat        //loop for heatsink cooling, display the cell voltage
    INTCON.GIE:=0;
    INTCON.GIE:=1;
    tw1:=twi;
    displ;
  until (keys.2=1);
  click;
  PORTB.0:=0;        //fan OFF
end;
// Discharge routine
procedure discharge;
begin
  cls;
  eeprom_write(uni_mode,mode_discharge);
  PORTB.0:=1;
  prepdis(0);
  case act of
    0:begin
        l:=eeprom_read(profile_point+pcutoff_nicd);
        tw:=l*10;
      end;
    1:begin
        l:=eeprom_read(profile_point+pcutoff_nimh);
        tw:=l*10;
      end;
    2:begin
        l:=eeprom_read(profile_point+pcutoff_lipo);
        tw:=2500+(l shl 2);
      end;
    3:begin
        l:=eeprom_read(profile_point+pcutoff_sla);
        tw:=1500+(l shl 2);
      end;
  end;
  tw1:=l*tw;        //ideal total cutoff voltage in mV
  action:=discharge_cc;                                                         //start the control
  sec:=0;
  minu:=0;
  mah:=0;
  keys:=0;
  pwm_err:=0;
  repeat
    INTCON.GIE:=0;
    twi:=slow_current-zero_current;
    INTCON.GIE:=1;
    tw1:=twi;
    displ;
    INTCON.GIE:=0;
    if (fast_voltage<target_voltage) then action:=idle;                         //exit when under cutoff voltage...
    INTCON.GIE:=1;
  until (action=idle) or (keys.2=1);
  action:=idle;
  sec:=0;
  tribeep;
  keys:=0;
  repeat
    INTCON.GIE:=0;                                                              //loop for heatsink cooling, display the cell voltage
    INTCON.GIE:=1;
    tw1:=twi;
    displ;
  until (keys.2=1);
  click;
end;
// PC management for internal parameters -> xx00.AAAA,xx01.BBBB,xx10.CCCC,1x11.DDDD -> write CCCC.DDDD at address AAAA.BBBB
// PC management for internal parameters -> xx00.AAAA,xx01.BBBB,xx10.xxxx,0011.xxxx -> read from address AAAA.BBBB
procedure pcmanage;
begin
  k:=0;
  l:=0;
  m:=0;
  cls;
  lcd_df_out(128,@msg_pcman1);                                                  //pc management message
//  lcd_df_out(192,@msg_pcman2);
  keys:=0;
  repeat
    if PIR1.RCIF=1 then                                                         //if an UART character has been received
      begin
        if (RCSTA and 6)<>0 then                                                //if there is an error
          begin
            j:=RCREG;
            j:=RCREG;
            RCSTA.CREN:=0;
            RCSTA.CREN:=1;                                                      //clear the error and flush the buffer
          end
        else
          begin
            eevar:=RCREG;                                                       //if no error read the value
            j:=(eevar and 0x30) shr 4;                                          //select the two bit xxAA.DDDD
            case j of
              0:begin
                  if (m=0) then m:=1 else m:=0;                                 // if AA=00 we have an address, first 4 MSB...
                  if (m=1) then
                    begin
                      k:=0;
                      k:=(eevar and 0x0F) shl 4;
                    end;
                end;
              1:begin
                  if (m=1) then m:=2 else m:=0;
                  if (m=2) then                                                 // then AA=01 we have  the 4 LSB...
                    begin
                      k:=k or (eevar and 0x0F);
                    end;
                end;
              2:begin
                  if (m=2) then m:=3 else m:=0;
                  if (m=3) then                                                 // if AA=10 we have the 4 MSB for data
                    begin
                      l:=0;
                      l:=(eevar and 0x0F) shl 4;
                    end;
                end;
              3:begin
                  if (m=3) then m:=4 else m:=0;
                  if (m=4) then
                    begin
                      l:=l or (eevar and 0x0F);                                 // if AA=11 we have the 4 LSB for data
                      if eevar.7=0 then                                         //the MSB of last byte selects between READ (0) or WRITE(1)
                        begin
                          l:=eeprom_read(k);
                          TXREG:=l;                                             //read from EEPROM and send to UART
                        end
                      else
                        begin
                          eeprom_write(k,l);                                    //write to EEPROM
                        end;
                      m:=0;
                    end;
                end;
            end;
          end;
      end;
  until (keys<>0);                                                              //repeat until keypressed
  click;
end;
// Profile display (display of chemistry, number of cells, capacity ...)
procedure display_profile;
begin
    case selitem of
    0:begin
        lcd_df_out(128,@msg_change1);
        lcd_df_out(192,@msg_change2);
        case l of
          nicd:lcd_df_out(139,@msg_change3);
          nimh:lcd_df_out(139,@msg_change4);
          lipo:lcd_df_out(139,@msg_change5);
          sla:lcd_df_out(139,@msg_change6);
        end;
      end;
    1:begin
        lcd_df_out(128,@msg_change7);
        lcd_df_out(192,@msg_change8);
        tw:=l*100;
        lcd_df_char(138,tmpword[0]);
        lcd_df_char(139,tmpword[1]);
        lcd_df_char(140,tmpword[2]);
      end;
    2:begin
        lcd_df_out(128,@msg_change9);
        lcd_df_out(192,@msg_change10);
        lcd_df_char(135,tmpbyte[1]);
        lcd_df_char(136,tmpbyte[2]);
      end;
    3:begin
        lcd_df_out(128,@msg_change11);
        lcd_df_out(192,@msg_change12);
        lcd_df_char(136,tmpbyte[0]);
        lcd_df_char(137,tmpbyte[1]);
        lcd_df_char(138,'.');
        lcd_df_char(139,tmpbyte[2]);
      end;
    4:begin
        lcd_df_out(128,@msg_change13);
        lcd_df_char(139,tmpbyte[0]);
        lcd_df_char(140,tmpbyte[1]);
        lcd_df_char(141,'.');
        lcd_df_char(142,tmpbyte[2]);
      end;
    end;
end;
// 8 bit Variable modify
procedure modvar(a:byte);
begin
  l:=eeprom_read(eevar);                                                        //read the variable
  if (a=0) then dec(l) else inc(l);                                             //modify
  if l=eelim then l:=eeres;                                                     //if below EELIM, saturate to EERES
  eeprom_write(eevar,l);                                                        //write back the value
end;
// Key mananegement during profile selection
procedure key_profile;
begin
    keys:=0;
    click;
    if (keys.0=1) then
    begin
      case selitem of
        0:begin
            eevar:=profile_point+pchemistry;
            eelim:=255;
            eeres:=0;
            modvar(0);
          end;
        1:begin
            eevar:=profile_point+pcapacity;
            eelim:=0;
            eeres:=1;
            modvar(0);
          end;
        2:begin
            eevar:=profile_point+pncells;
            eelim:=0;
            eeres:=1;
            modvar(0);
          end;
        3:begin
            eevar:=profile_point+pcharge;
            eelim:=0;
            eeres:=1;
            modvar(0);
          end;
        4:begin
            eevar:=profile_point+pdischarge;
            eelim:=0;
            eeres:=1;
            modvar(0);
          end;
      end;
    end;
    if (keys.1=1) then
      begin
        case selitem of
          0:begin
              eelim:=4;
              eeres:=3;
              modvar(1);
            end;
          1:begin
              eelim:=0;
              eeres:=255;
              modvar(1);
            end;
          2:begin
              eelim:=20;
              eeres:=19;
              modvar(1);
            end;
          3:begin
              eelim:=0;
              eeres:=255;
              modvar(1);
            end;
          4:begin
              eelim:=0;
              eeres:=255;
              modvar(1);
            end;
        end;
      end;
      if (keys.2=1) then
        begin
          inc(selitem);
        end;
end;
// Battery profile change
procedure changeprofile;
begin
  selitem:=0;
  repeat
    display_profile;                                                            //display the current item in the profile
    key_profile;        //change it
  until (keys.2=1) and (selitem=5);
end;
// Procedure default values
procedure default_values_pack;
begin
  j:=k*profilelen;
  eeprom_write(j+pchemistry,0);                                                 //Default NiCd (0) -> 0:NiCd, 1:NiMh, 2:LiPo, 3:SLA
  eeprom_write(j+pcapacity,30);                                                 //Default cells capacity (30) -> 30*100=3000mAh
  eeprom_write(j+pncells,6);                                                    //Deafult number of cells (6) -> 6
  eeprom_write(j+pcharge,10);                                                   //default charge (10) -> 3000*1.0=3A
  eeprom_write(j+pdischarge,40);                                                //default discharge (40) -> 3000*4.0=12A
  eeprom_write(j+pinhibit,5);                                                   //default deltapeak check inhibition (5) -> 5 minutes
  eeprom_write(j+pcutoff_nicd,80);                                              //default NiCd cutoff (80) -> 80*10=800mV
  eeprom_write(j+pcutoff_nimh,100);                                             //default NiMh cutoff (100) -> 100*10=1000mV
  eeprom_write(j+pcutoff_lipo,125);                                             //default LiPo cutoff (125) -> 2500+125*4=3000mV
  eeprom_write(j+pcutoff_sla,125);                                              //default SLA cutoff (125) -> 1500+125*4=2000mV
  eeprom_write(j+pdeltav_nicd,10);                                              //default NiCd deltapeak (10) -> 10mV
  eeprom_write(j+pdeltav_nimh,5);                                               //default NiMh deltapeak (5) -> 5mV
  eeprom_write(j+pmaxv_lipo,175);                                               //default LiPo max voltage (175) -> 3500+175*4=4200mV
  eeprom_write(j+pmaxv_sla,125);                                                //default SLA max voltage (125) -> 2000+125*4=2500mV
  eeprom_write(j+pfinalcurr_lipo,5);                                            //default LiPo final current (5) -> 3000*5/100=150mA
  eeprom_write(j+pfinalcurr_sla,5);                                             //default SLA final current (5) -> 3000*5/100=150mA
  eeprom_write(j+ptimeout,120);                                                 //default cell max charge (120) -> 3000*120/100=3600mAh
end;
procedure default_values_uni;
begin
  eeprom_write(uni_profile,0);                                                  //Default profile selected (0) -> 1st profile
  eeprom_write(uni_maxcharge,5);                                                //Default max charge current (5) -> 5A
  eeprom_write(uni_maxdischarge,20);                                            //Default max discharge current (20) -> 20A
  eeprom_write(uni_beep,25);                                                    //default beep tone semiperiod (25) -> 25*10=250us (2000Hz)
  eeprom_write(uni_r5h,183);                                                    //default (183)
  eeprom_write(uni_r5l,152);                                                    //default (152) R5=R5h*256+R5l = 47000 Ohm
  eeprom_write(uni_r6h,46);                                                     //default (46)
  eeprom_write(uni_r6l,224);                                                    //default (224) R6=R6h*256+R6l = 12000 Ohm
  eeprom_write(uni_currh,97);                                                   //default (97)
  eeprom_write(uni_currl,168);                                                  //default (168) Curr=Currh*256+Currl= 25000 -> 25000uv/A
  eeprom_write(uni_mode,mode_idle);                                             //default mode (0) -> idle
  for k:=0 to 15 do eeprom_write(uni_firstline+k,msg_hello1[k]);                //default hello message 1st line -> ".seven-segments."
  for k:=0 to 15 do eeprom_write(uni_secondline+k,msg_hello2[k]);               //default hello message 2nd line -> "www.        .com"
end;
// 16 bit Variable modify
procedure modvar16(a:byte);
begin
  tw:=eeprom_read(eevar);
  inc(eevar);
  tw:=tw+(eeprom_read(eevar) shl 8);
  if (a=0) then tw:=tw+10 else tw:=tw-10;
  eeprom_write(eevar,hi(tw));
  dec(eevar);
  eeprom_write(eevar,lo(tw));
end;
// Calibration procedure (Volt and Ampere)
procedure calibration(a:byte);
begin
  cls;
  calibra:=1;
  PORTB.0:=1;
  prepdis(2);
  tw1:=200;
  if (a=0) then
    begin
      action:=idle;
      eevar:=uni_r6l;
    end
  else
    begin
      action:=charge_cc;
      eevar:=uni_currl;
    end;
  keys:=0;
  repeat
    INTCON.GIE:=0;
    INTCON.GIE:=1;
    tw1:=twi;
    displ;
    if (keys.0=1) then
      begin
        modvar16(0);
        keys:=0;
        click;
      end;
    if (keys.1=1) then
      begin
        modvar16(1);
        keys:=0;
        click;
      end;
  until (keys.2=1);
  action:=idle;
  click;
  calibra:=0;
  PORTB.0:=0;
end;
// Main program, neverending loop
begin
     ADCON0:=0x81;                                                              //PIC hardware related variables init
     INTCON:=0x20;
     RCSTA:=0x90;
     CCPR1L:=0x0;
     CCPR2L:=0x0;
     T2CON:=0x4;
     CCP1CON:=0xC;
     CCP2CON:=0xC;
     OPTION_REG:=0x6;
     SPBRG:=0x81;                                                               //9600 baud @20MHz
     TXSTA:=0xA4;
     ADCON1:=0x84;
     TRISA:=0x0B;
     TRISB:=0xE0;
     TRISC:=0x80;
     PR2:=0xFF;
     PORTA:=0xFF;
     PORTB:=0x0;
     PORTC:=0x0;
     repeat_k1:=0;
     repeat_k2:=0;
     repeat_k3:=0;
     action:=0;
     duty_pwm_charge:=0;                                                        //all off
     profile_point:=0;
     calibra:=0;        //no calibration at startup
     lcd_df_config;
     j:=eeprom_read(uni_profile);
     if j=255 then                                                              //if the EEPROM is unprogrammed, program for defaults
       begin        //writing 255 to the profile selection address the default is reloaded
         default_values_uni;
         for k:=0 to 11 do default_values_pack;
       end
     else profile_point:=j*profilelen;                                          //else restore the current profile
     lcd_df_out_eeprom(128,uni_firstline);
     lcd_df_out_eeprom(192,uni_secondline);
     beep;
     k:=0;
     keys:=0;
     repeat
       inc(k);        //wait for user action or timeout for interrupted action restart
       delayms(10);
     until (keys<>0) or (k=255);
     if keys<>0 then click;
     keys:=0;
     if (k=255) then                                                            //if no key pressed resume the last operation (if any)
       begin
         phase:=eeprom_read(uni_mode);                                          //read if there is a suspended action
         if (phase=mode_charge) then                                            //if a precededent action was suspended by a power loss,
           begin        //complete it
             charge;                                                            //finish the discharge
           end;
         if (phase=mode_discharge) then
           begin
             discharge;                                                         //finish the discharge
           end;
       end;
     eeprom_write(uni_mode,mode_idle);                                          //abort the last action, if necessary
     menupos:=0;        //start display from "profile selection"
     repeat
       main_menu;                                                               //display the main menu and check the keys
       case menupos of
         0:selprofile;                                                          //battery pack profile selection routine
         1:charge;                                                              //charge the battery
         2:discharge;                                                           //discharge the battery
         3:changeprofile;                                                       //Actual battery pack profile change
         4:pcmanage;                                                            //PC control on parameters
         5:calibration(0);                                                      //Voltage calibration
         6:calibration(1);                                                      //Current calibration
       end;
     until false;                                                               //neverending loop
end.